I would recommend to double check the algorithm and make sure that is able to output negative values. You should post your pid code.
The approach you are using is a simple and quite effective control strategy in which the knowledge of the model is not required to get the job done. By 'knowledge of the model' I mean the system of equations that describes the dynamics of your quadcopter in space. You just need the reference value, the filtered measurement (the estimated angle) and three coefficients.
In your project you want your roll and yaw angle to be 0, at least in hovering mode right. Let's consider as a measured variable y(t), the roll angle theta(t) at time t (the pitch angle phi will be another one). So y(t) = theta(t).
- First of all, make sure that your estimated angles are accurate.
Then define the control error as the difference between the desired position, y_des = 0, and the actual measurement at time t, y(t).
e(t) = y_des - y(t)
In order to understand the effect of each coefficient, (Kp,Kd and Ki) we need to look at the control formula.
The control input u(t) is the sum of three different terms:
The proportional term is described by the Kp gain which tells the control how intense should the response be compared to the error. What does it mean? If at time t, the quad is 3 degree away from your setpoint (e(t)=3) then apply a torque Kp times that value to get it back the correct position. If the value is to high you will pass your set point and you will notice oscillations around the 0 value. The steady state error will decrease with increasing gain, but the tendency towards oscillation will also increase. You can't get good results only with this term.
The derivative term is characterized by the Kd gain. In the formula, this coefficient is multiplied by the derivative of the error. In other words, this gain tells the controller how fast should it react to changes in error's values. If you are going away from your set point, the error's derivative will be different than zero and positive (or negative) so apply a torque proportionally to this value. The derivative action will not help if the sample time is too large.
The integral term is described by the Ki gain. This coefficient weights the contribution of how long does the quadcopter remains in a state of error. If you are testing the control only on one axis and you are using a too low Proportional gain, Kp, you will notice that the quad won't be able to reach the 0 degree reference value and will be "stuck" at a certain angle. Adding Ki != 0 will help by providing an extra torque value after an interval of time. The Ki gain will determine this extra torque value.
Here is example using arduino. (This is a basic code and what's above is pub version of the explanation)
// Roll PID
errorRoll = abs(SetpointRoll - estimatedKalmanRoll); //distance away from setpoint
if(errorRoll<thresholdRoll)
//we're close to setpoint, use conservative tuning parameters
myRollPID.SetTunings(consKpRoll, consKiRoll, consKdRoll);
else
//we're far from setpoint, use other parameters
myRollPID.SetTunings(aggKpRoll, aggKiRoll, aggKdRoll);
myRollPID.Compute(); // This computes rollpid
Same thing for pitch, yaw and altitude
// computes motor IN based on roll, pitch, yaw Pid OUT and throttle value
motorA = thr + rollpid - yawpid;
motorB = thr + pitchpid + yawpid;
motorC = thr - rollpid - yawpid;
motorD = thr - pitchpid + yawpid
Check this answer as well.
Hope this helps,
Ciao.